residential electric, 12 volts from neutral to ground on receptacle

im getting 120v from hot to neutral
hot to ground is 70v sometimes low as 55
neutral to ground 12v

also my plug in outlet tester shows correct (two gold lights however the right gold light is blinking)



i appreciate the help


__________________
 
Reply With Quote
Sponsored Links

Download SOLAR SECRETS by Peter Lindemann
Free - Get it now: Solar Secrets

  #2  
Old 08-09-2018, 05:48 PM
ewizard's Avatar
ewizard ewizard is offline
Gold Member
 
Join Date: Jan 2010
Location: Outside the Matrix
Posts: 1,109
Digital voltmeter? Old house? 120 volts hot to neutral is about right but it sounds like you have a poor ground. Is you house ground rod in very dry ground? Connections on the ground solid and free of corrosion? check your incoming ground to the electric panel also -- be careful if you have to pull the panel cover. Neutral to ground should be 0 volts but sometimes a ghost voltage will appear which has essentially no current to it. You may want to get another copper plated 8 foot ground rod to install and parallel it onto the existing ground wire going the the main electric panel - may want to have an electrician do that.
__________________
There is no important work, there are only a series of moments to demonstrate your mastery and impeccability. Quote from Almine
Reply With Quote
  #3  
Old 08-09-2018, 06:23 PM
johnnyfalcon johnnyfalcon is offline
Senior Member
 
Join Date: May 2014
Posts: 131
Quote:
Originally Posted by ewizard View Post
Digital voltmeter? Old house? 120 volts hot to neutral is about right but it sounds like you have a poor ground. Is you house ground rod in very dry ground? Connections on the ground solid and free of corrosion? check your incoming ground to the electric panel also -- be careful if you have to pull the panel cover. Neutral to ground should be 0 volts but sometimes a ghost voltage will appear which has essentially no current to it. You may want to get another copper plated 8 foot ground rod to install and parallel it onto the existing ground wire going the the main electric panel - may want to have an electrician do that.
yes a digital mm
house is not old like 1972

i get these measurements on each of the 3 different receptacles in my dining room only


im going to check as many variables as i can, i find this vary strange since everything works ill tighten up some wires in the panel maybe
__________________
 
Reply With Quote
Reply

Tags
gold, ground, hot, neutral, receptacle, electric, volts, residential

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off



Please consider supporting Energetic Forum with a voluntary monthly subscription.

For One-Time Donations, use admin@ this domain > energeticforum.com

Choose your voluntary subscription

All times are GMT. The time now is 09:06 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2018, vBulletin Solutions, Inc.
Search Engine Optimisation provided by DragonByte SEO v1.4.0 (Pro) - vBulletin Mods & Addons Copyright © 2018 DragonByte Technologies Ltd.
Shoutbox provided by vBShout v6.2.8 (Lite) - vBulletin Mods & Addons Copyright © 2018 DragonByte Technologies Ltd.
2007-2015 Copyright - Energetic Forum - All Rights Reserved

Bedini RPX Sideband Generator

Tesla Chargers